Why miners want 240V not 110V, breaker math, plug types, and the IP/VLAN/DNS scheme that keeps a fleet reachable.
Power steps down through several stages before it reaches a miner. Knowing the chain tells you where a fault lives.
Use only an OEM-approved supply. For single-phase AC, P = V × I × PF; at constant real power and power factor, doubling voltage halves current. The table assumes PF = 1 and is an estimate, not installation sizing. Balanced three-phase total power uses P = √3 × V(line-line) × I × PF. Follow rated maximum input-current and installation requirements; qualified measurements supplement them.
| Miner draw | @208 V | @240 V | @277 V |
|---|---|---|---|
| 3,000 W | 14.4 A | 12.5 A | 10.8 A |
| 3,250 W | 15.6 A | 13.5 A | 11.7 A |
| 3,500 W | 16.8 A | 14.6 A | 12.6 A |
In the standard-rated NEC-style continuous-load example, load is limited to 80% of breaker rating (125% sizing). Properly applied 100%-rated assemblies and local rules can differ; qualified design must also cover conductors and equipment.
| Connector | Rating | Use |
|---|---|---|
| C13 / C14 | 250 V, ~15 A | Standard miner cord |
| C19 / C20 | 250 V, ~20 A | Modern high-watt ASICs |
| NEMA L6-30 | 250 V, 30 A | Twist-lock PDU (vibration-proof) |
| IEC 60309 | 16-60 A 3Ø | Industrial PDU feeds |
A fleet needs a stable, isolated network where every miner maps to a physical location.